I was wondering if any of you have any experience burying galvanised steel conduit?

My current plan is to make up the conduit, T-Wash it and give it a couple of coats of primer and hammerite before I sink it in the ground but I'm wondering if it will be enough? My Father has suggested covering it in heat shrink before it is buried? Is it needed?

The conduit will be the only CPC to an outbuilding so it's essential it cannot corrode over time.

And yes, I could run an SWA but I don't want to. :p

Sam
 
I was wondering if any of you have any experience burying galvanised steel conduit?

My current plan is to make up the conduit, T-Wash it and give it a couple of coats of primer and hammerite before I sink it in the ground but I'm wondering if it will be enough? My Father has suggested covering it in heat shrink before it is buried? Is it needed?

The conduit will be the only CPC to an outbuilding so it's essential it cannot corrode over time.

And yes, I could run an SWA but I don't want to. :p

Sam
SWA would be my choice, why the reluctance to use it?
 
If you must use conduit, then I would pull in a separate CPC. I have come across several instances where conduits buried in concrete/ plaster have failed miserably in regards to acting as an earth, although they are 40/50 years old....install a separate earth conductor.
 
The conduit will be the only CPC to an outbuilding so it's essential it cannot corrode over time.Sam

What you are proposing to do is not acceptable.

If you are a spark you should know this, if you think you will be getting a spark to sign it off - they won't

Would you fit worn out tyres to a brand new car and race it around a track?
 
I once came across a 95mm 4 core SWA (installed 2007) where which was ran underground in a duct from a substation, ran downhill to a building. Where it was glanded into the section board was completely corroded as were the SWA armouring strands, could only presume the outer insulation was damaged during installing in the duct, and water has got in, and wicked its way out of the gland...luckily there was a separate earth cable installed!
 
The conduit may corrode rapidly due to galvanic action with other earthed metalwork. I went to investigate one buried steel conduit only to find it had been completely eaten away, leaving singles buried direct in the earth. If I had to bury steel for whatever reason,I would wrap the whole length in Denso tape, but there are much better alternatives!
 
The conduit may corrode rapidly due to galvanic action with other earthed metalwork. I went to investigate one buried steel conduit only to find it had been completely eaten away, leaving singles buried direct in the earth. If I had to bury steel for whatever reason,I would wrap the whole length in Denso tape, but there are much better alternatives!
Like SWA cable?
 
When you say "cps" do mean main earth - exporting pme? What's in the outbuilding services wise? does anything need bonding?

You are not normally allowed to export the PME, I believe you mean extending the Equipotential Zone of which is something totally different.

As others have commented here, your over complicating the issue and creating problems for yourself here, the 2 common methods are to bury some ducting and pull your cabling through (usually SWA) or bury SWA directly, any other method like you suggest becomes a very expensive solution due to all the extra protection required to combat the natural corrosion and moisture ingress.
 
Last edited:
To export the PME would in essence mean continue the DNO supply method (normally concentric cable) where the N/E are combined to another location, the thread link you posted only goes to show the confusion what is exactly meant by the term Exporting PME, I totally disagree with what the thread suggests as it takes on the idea you are simply bringing an earth out of your property to say a garage from your supply origin but this is no longer classed as a PME as all wiring you do after the cutout is Seperate N/E thus not classed as PME and therefore cannot be addressed as exporting PME.
If you wished to continue the PME system then you would need to inform the local DNO as local networking conditions may require additional measures to be taken, it is not a no go solution but it is very rarely asked for or done due to the extra time and work it can involve when there are simply easier, quicker and cheaper solutions.

A buildings equipotential zone is usually the perimeter structural wall of the installation IE, if you take a supply passed this perimeter to say a remote shed with an earth then you are said to be extending the equipotential zone to that shed, it is just a descriptive change and usually makes no difference to the installation.
 

Reply to Burying Galvanised Steel Conduit in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock