Tenant reported that his fuse box caught fire. I found this stove circuit pullout. This unit was built in the 60s wired in aluminum but I found no corrosion and no indication of foil or other foreign material in the box.. The fuses are Bussman NON-35 Amp. Probably the original fuse from the 50s. I installed a new breaker box.
Never seen or heard of this. Any suggestion what happened?
16626495818932274062019981283442.jpg
 
Most likely cause is that high resistance had developed at one of the fuse end caps, which began to arc and burn material away until enough heat was being generated to scorch the phenolic moulding. There is a notch in the end cap that suggests it was the fuse element arcing to the end cap, although I suspect the initiating failure was more likely to be high resistance to the pull-out contact.
 

Reply to Bussman NON-35 fuse fire? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Life is is clearly circular. A few months ago I can across in service a 1940s ish steel enclosed MEM "fuse box" and this week when doing a...
Replies
0
Views
842
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
78K
Ok, so I'm registered with Rated People. I don't use them very often but once or twice I have purchased a lead that has turned out to be very...
Replies
28
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock