Search the forum,

Discuss Comsumer unit - upstairs/downstairs ring mains in the UK Electrical Forum area at ElectriciansForums.net

taconite1

DIY
Reaction score
4
Hello,

I bought a new build and noticed the upstairs MCB is controlling some sockets on the opposite floor, so if I flick the upstairs MCB it's also switching off a socket downstairs (I think it's a spur) in addition to all the ones upstairs

Is there anything within 7671 that states this is wrong?

I asked the contactor on site and they said it can be re-wired but it's down to my prefrence. Is this correct? Surely the regs have something to say on this.

P.S this same contractor didn't earth some of the metal faceplate light switches (including backbox) - so I don't trust them at all. Despite having a NIC form filled in and signed by two qualifed electricans!!
 
Last edited:
Nothing wrong with having sockets on different floors wired on the same MCB as long as the labelling on the CU reflects this or doesn't mention 'upstairs' or 'downstairs' at all.
I've almost always grouped socket circuits in downstairs rooms with the rooms directly above, except for kitchens and utility rooms.
 
Nothing wrong with having sockets on different floors wired on the same MCB as long as the labelling on the CU reflects this or doesn't mention 'upstairs' or 'downstairs' at all.
I've almost always grouped socket circuits in downstairs rooms with the rooms directly above, except for kitchens and utility rooms.
Hi nope it has stickers for upstairs and downstairs
 
It is an odd thing to do but nothing wrong with it, might gave been done if the other circuit failed you still have one close by working. Metal switch front plates not being earthed is a big issue.
 
They should both be earthed. I wonder if the other properties are the same, this sort of thing is fundamental.
I asked that question but they wouldn't answer!! It would open a can of worms regarding rework!

Our house was probably the 15th built on site so if they got this far and are making mistakes like that - it does make you wonder
 
They should both be earthed. I wonder if the other properties are the same, this sort of thing is fundamental.
I always fit a fly lead on both switches and sockets, but the last time I looked it was apparently considered acceptable to earth the plate and rely on the fixing screws to earth the box, provided one of the fixings in the box is 'fixed' and not the adjustable (to level the fitting) type.
 
Are the building company still on site?
They are. I asked one why it wasn't earthed correctly and he said it was an "oversight". It's fixed now (I basically told them to go around with a tester and touch each light switch for earth) but as a homeowner why am I picking these things up? Hence my concerns now with the MCBs on the consumer unit.
 
They are. I asked one why it wasn't earthed correctly and he said it was an "oversight". It's fixed now (I basically told them to go around with a tester and touch each light switch for earth) but as a homeowner why am I picking these things up? Hence my concerns now with the MCBs on the consumer unit.
Pic attached - found 6 more like this
IMG_1096.jpg
 

Reply to Comsumer unit - upstairs/downstairs ring mains in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top