Hi guys, just dropped into a care home and they have a 24v fail safe door catch that’s intermittent not releasing so dropped into a supplier on my way home to grab a replacement and was going to go in tomorrow to swap it over.
Just looked at the new catch and it’s a 12v latch! Tried calling the supplier to see if they have a 24v and getting no answer
Will the 12v catch be ok to use or should I blast back in the morning and grab a 24v?
It’s a real pain in the --- as it will be at least an hour or so round trip.
Cheers!
Just looked at the new catch and it’s a 12v latch! Tried calling the supplier to see if they have a 24v and getting no answer
Will the 12v catch be ok to use or should I blast back in the morning and grab a 24v?
It’s a real pain in the --- as it will be at least an hour or so round trip.