A very common cause of pressure loss in the heating system is a leaking PRV (pressure release valve). That's the thing with the red conical knob, just behind the pressure gauge.
The copper pipe to the left of the PRV, running slightly downhill and then forwards, should go outside and have an open end, like an overflow pipe. If there is water occasionally dripping from it, then the PRV is the problem.
Thank you again for the replies. So have found the problem - One of the bedroom radiators has a tiny pinhole leak from the pipe that leads to the radiator. The pipes leading to the radiators go along the wall beside the radiators and through the wall. From what I can see the leak is coming from one of the nuts on the pipe leading to the radiator.
I have wrapped the hole/leak with waterproof tape and wrapped a towel around it for now to try to stop the leak, and have turned off the heat control knob for that radiator. Is there anything else I can try to stop the leak - Should I try to tighten the nut where the leak is coming from? Or is there any other valve I can switch off somewhere on the radiator?
Difficult to say. You could try tightening it, but don't over do it. Try and hold the radiator valve body with an adjustable spanner while you do it. The valve will have a flat section to allow this.
The temperature control knob is on the opposite side of radiator. Does the other smaller knob, on opposite side to radiator have any purpose at all?
To try to tighten the nut on the pipe near the radiator, do I turn it to the right, or the left? As do not want to loosen it by mistake.
The valve on the other side is called a lockshield valve, and it is used when balancing the radiators so that they all give equal heat out. You wouldn't adjust it yourself.
The threads are standard right hand threads, so tighten as you would a normal nut on a bolt.
I am not experienced with tightening nuts in general, but I do have a tool box... I do not want to cause a flood by loosening the nut.... Is it generally left for loose and right for tight?
RENTED!
Get the landlord to deal with it.
1. He pays
2. If it goes wrong, it his responsibility.
righty tighty, lefty loosey
not all landlords are evil land barons... They might actually have a service plan in place that covers repairs
righty tighty, lefty loosey
not all landlords are evil land barons... They might actually have a service plan in place that covers repairs
righty tighty, lefty loosey
not all landlords are evil land barons... They might actually have a service plan in place that covers repairs
Absolutely. Landlords seem to be a popular target of hate these days, but I could tell you a couple of stories about some interesting tenants!
I am sure, but I could guarantee that as my experiences of a private tenant, I could absolutely trump those stories. The "rouge" landlords far outweigh the good ones unfortunately.
I'm out of this thread. Bye.
Sorry you feel that way... Your judgment towards me seems to have changed since I stated that I was a tenant, rather than homeowner... Discrimination is very sad, and very unfounded.
Could anybody please advise - I currently have the heating control knob for the leaking radiator turned off, but I really do need heat in that room... Does having the heating control knob for that radiator turned on or off make any difference at all to the water leak from the nut on the pipe?
I apologise. I didn't mean to come across that way. Ignore my previous comment. I've been reading a few anti-landlord comments on a BBC news story comments.
Stay on here - you'll get good advice.
if you desperately need immediate heat from that radiator, you only have one option.
turn on the radiator valves, it will leak and you will have to collect or deal with the water that is coming out.
the boiler will slowly lose pressure as the water leaks, so you will have to continue to top up the system when the pressure drops.
the correct and final fix is to replace the item that is leaking, it may be a pipe or a valve, or a radiator.
realistically, if you intend to do it yourself, you must identify the failed component and replace it with a new one.
if not then it is a case of report it to the land lord and wait for a permanent repair, NOTE- this does not prevent you from constantly topping up the system so that it continues to work.
however, be aware that leaks can cause other damage so must be contained.
The most likely cause of the leak is that the radiator has been knocked and has moved on its brackets, and a quarter turn or less of the nut will solve the problem, although the black tape is worrying. Was that there before the current leak?
Reply to Heating Lost Pressure in the Central Heating Systems area at ElectriciansForums.net