How to test a circuits in steel conduit as the cpc

Discuss How to test a circuits in steel conduit as the cpc in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
16
Good evening

I am currently a training to become an electrician. I do hold both initial verification and periodic testing qualifications however this is an issue I have never personally had to deal with and was never mentioned on any of my courses as often seems to be the case.

Basically I am wondering how you would hypothetically go about testing either a ring or radial circuit if you didn't have a seperate cpc but the conduit itself acted as this.

Look forward to hopefully getting a response and some clarity

Regards Harry
 
For a radial circuit you can calculate R2. If you measure the continuity of the line and neutral then divide in half this will give you R1 assuming the line and neutral are of the same length. Then measure R1 + R2 and deduct your first reading which should give you an approximate R2. For a ring final circuit you cannot do an r2 for the cpc as you have no end to end as such but you can use the same principle to to calculate R2 from the farthest point.
 
R2 being the CPC I don't think you should be calculating it.
There is nothing wrong with my suggestion, you are using various measurements and using some calculations to extract R2. Using a wander lead and subtracting the leads resistance is no different as this is also a calculation.
 
During the design stage it is very much acceptable to calculate R1+R2 and necessary in most of, if not all cases
I’m not talking about the design stage. I’m talking about testing on site. We should be avoiding live testing whenever possible. And doing an R1+R2 test. Then calculate the ZS. Not always possible I know but the NIC I believe are trying to get this pushed forward because people are working live on steps trying to do a ZS and having accidents
 
How do you measure R2 with no calculation. Your own method not how the NIC think it should be done.
What calculation would you need to do to perform an R2 test? You need to Null the wandering lead first if that’s what your referring to?
During the design stage it is very much acceptable to calculate R1+R2 and necessary in most of, if not all cases
also I personally think that a measured R1 +R2 test gives a more true reading than a ZS because a Zs is influenced by potential parallel paths that will lower the reading. And as we know parallel paths can be removed. If this occurred the ZS could potentially raise above the acceptable level for the circuit/ protective Device.
 
What calculation would you need to do to perform an R2 test? You need to Null the wandering lead first if that’s what your referring to?

also I personally think that a measured R1 +R2 test gives a more true reading than a ZS because a Zs is influenced by potential parallel paths that will lower the reading. And as we know parallel paths can be removed. If this occurred the ZS could potentially raise above the acceptable level for the circuit/ protective Device.
Parallel paths will in most cases result in a lower result of zs than the calculation of zs=ze+(R1+R2) rather than a higher value
 
Problem here, is that we work to BS7671, not to the NICEIC regulations.
There are no tables of maximum R1+R2 in BS7671, there are only tables for maximum Zs.
So it’s all very well measuring R1+R2 and adding it to Ze, but what do you do if that value is above the maximum permissible?
What you do is rewire the circuit or design it better. Or use a B type MCB but only if the circuit is adequate for a B type MCB. If it’s a Condition report surely it’s a C2 if a circuit fails max Permissible Zs. I fail to see your point anyway because a circuit can still fail doing a Zs test. We shouldn’t be relying on parallel paths to get circuits to pass. Even thow it is done, doesn’t make it right.
 
How can say the circuit has failed max Permissible Zs if you’ve only calculated the Zs?
You’ve just admitted that Zs can be affected by parallel paths, so unless you measure the Zs, you cannot say whether the circuit fails or not.
There’s no prohibition in BS7671 against using parallel paths.
 
How can say the circuit has failed max Permissible Zs if you’ve only calculated the Zs?
You’ve just admitted that Zs can be affected by parallel paths, so unless you measure the Zs, you cannot say whether the circuit fails or not.
There’s no prohibition in BS7671 against using parallel paths.
You do the R1 +R2 + Ze and if it fails that then you measure Zs to see if that passes. I didn’t say never do a Zs, my point was to reduce the amount of live testing and also more importantly never calculate your R1+R2. If you calculate your R1 +R2 your calculating it from a measured Zs that could be affected by parallel paths. So it’s not a true R1+R2 reading. Only a measured R1 +R2 is a true reading.
 
Hi,and don't forget to do the inspection part,as,if containment is effectively,a CPC, with possibly dozens of "connections",it may pass the testing,but could give a visible indication,of not being capable of sustaining a higher,fault current.
A ductor tester should be used to check the condition of the conduit joints. Test current of 100A should be fine.
 
With a wandering earth lead. If I explain any further I feel that I am teaching you to suck eggs.
I’ve had that feeling every time I’ve replied to a comment lol. On a serious note I feel that some people who are doing EICRs are not clued up enough to be doing them. But I’m happy to help anyone out. We all have to learn and help each other out. Two heads are better than one.
 

Reply to How to test a circuits in steel conduit as the cpc in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top