Discuss Legality of using a lighting circuit to power an observatory? in the DIY Electrical Advice area at ElectriciansForums.net

dgstrange

DIY
Reaction score
1
I have a lighting circuit cable (1mm) powering a telescope (12 volts) in an observatory total draw 84 watts drawn from a transformer. There is a 6 amp fuse in the consumer unit. This was installed in 1998 by a qualified electrician. Is this still legal or should it be upgraded?
Thanks
 
Courtesy of a recent change in the regs, it wasn't allowed then, but it is now.
Up until the change, the minimum csa, for anything other than a lighting circuit, was 1.5mm2, but now that's changed to 1.0mm2.
There may be, of course, other things that could do with improvement by now, but this isn't one of them (anymore).
 
Last edited:
Courtesy of a recent change in the regs, it wasn't allowed then, but it is now.
Up until the change, the minimum csa, for anything other than a lighting circuit, was 1.5mm2, but now that's changed to 1.0mm2.
There may be, of course, other things that could do with improvement by now, but this isn't one of them (anymore).
Many thanks, that is very useful to know! Would you by any chance be able to provide a link to those regulations?
 

Reply to Legality of using a lighting circuit to power an observatory? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
508
Hi My main feed comes into the garage, feeds into the meter and then out to another box with a 60AMP fuse then into the house...
Replies
20
Views
3K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
456
Hi everyone. The title should sound crazy enough, but it's what happening in my 72-years old home we've purchased 2 years ago. I found the crazy...
Replies
1
Views
506
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock