I'm having issues with finding our Maglocks in the released position every morning (7 am). This was happening for a few weeks and they would be found in the released position with no history of power outage, Fire incident or brown out on the Fire Panel. After inspections, neither the Fire techs or Alarms techs could locate the issue. A couple weeks ago it appeared that the problem had fixed itself and the Maglocks were in the secured position but again this morning they were in the unsecured position. I will put back in the secure position using the key switch and they will hold all day. As it's not a 24 hour operation, there is no record of the exact time they would go in the unsecured postion (release). I have 4 Maglocked doors with two powered revolving doors. Has anyone experienced this or could shed some light as my Fire contract and Alarm contract are not resolving the issue. Thanks
 
I’m expecting the mag locks to be “always on” and the fire alarm signal simply a relay that turns off the power to the locks.
Also likely that it’s only 12 or 24v to the magnets.

A “just” loose connection or a broken cable could cause the intermittent loss of power anywhere on the circuit, not just at the relays in the fire panel.

Is there any machinery that might start up overnight where vibration throughout the building might dislodge the connection momentarily.
 
I’m expecting the mag locks to be “always on” and the fire alarm signal simply a relay that turns off the power to the locks.
Also likely that it’s only 12 or 24v to the magnets.

A “just” loose connection or a broken cable could cause the intermittent loss of power anywhere on the circuit, not just at the relays in the fire panel.

Is there any machinery that might start up overnight where vibration throughout the building might dislodge the connection momentarily.
All correct on the 'always on' and require 24v to the magnets. I've asked my Security (FOB access) team to test each power connection. The only place that vibration might happen is on the Loading dock MAG but nothing in that area that would happen overnight. Still stumped but hopefully they find the issue. Apparently the Power supply is from an old access control system and they cut corners and reused it instead of installing a new one. Thats where we're starting.
 
If the power supply unit is suspect, it might be just able to support the system load under good conditions, but when the voltage from the utility supply varies e.g. as the daytime load comes on suddenly, it drops out, which could explain the daily cycle of releasing.
 
I'm having issues with finding our Maglocks in the released position every morning (7 am). This was happening for a few weeks and they would be found in the released position with no history of power outage, Fire incident or brown out on the Fire Panel. After inspections, neither the Fire techs or Alarms techs could locate the issue. A couple weeks ago it appeared that the problem had fixed itself and the Maglocks were in the secured position but again this morning they were in the unsecured position. I will put back in the secure position using the key switch and they will hold all day. As it's not a 24 hour operation, there is no record of the exact time they would go in the unsecured postion (release). I have 4 Maglocked doors with two powered revolving doors. Has anyone experienced this or could shed some light as my Fire contract and Alarm contract are not resolving the issue. Thanks
Problem finally resolved. After switching a relay in the fire panel, and then switching the power supply for the mag locks, the issue was with the key switch. There appeared to be another relay for the key switch. Once changed we haven’t had a problem since.
 

Reply to Maglocks all releasing in the Electricians' Talk | All Countries area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock