Evening everyone…
I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in situ..
they want an outside socket.. I’ve told them that I can’t install one as there’s no RCD.. they’re asking if there’s any alternative ways safely around this as they can’t fork out for a new DB.. the socket on the interior.. if I was to change this to an RCD socket faceplate.. could I then Spur off this to an outside socket? This would mean the socket downstream is RCD protected right?
 

Attachments

  • fa4c586e-693e-4e33-ba85-9ce3b2b3f3b7.jpeg
    98.2 KB · Views: 26
  • 90b45717-62c9-4822-aaa2-6ac067481124.jpeg
    84.9 KB · Views: 23
  • b39fdbcd-9124-4452-961b-a72e0c390ee2.jpeg
    191.1 KB · Views: 23
Electric showers with no rcd make me shudder since seeing the state immersion elements can get in with no rcd 😳 rcd socket outside may get you out of a muddle if you want the job and if your going straight through, I'd probably stick a bit of conduit through the cavity to give the t/e a teeny bit more protection too.
 
Check supply earthing before you touch it. Not clear photo but I’d check it isn’t TT with no fault protection.

While fitting an RCD socket ticks the additional protection box, the cable can need RCD protection too for impact protection.
I don’t like doing this but a a surface box RCD spur inside covers the cable, the socket and the load.
 
Electric showers with no rcd make me shudder since seeing the state immersion elements can get in with no rcd 😳 rcd socket outside may get you out of a muddle if you want the job and if your going straight through, I'd probably stick a bit of conduit through the cavity to give the t/e a teeny bit more protection too.

I seem to find two types of installation in older houses in which electric showers have been added: those with shower fed from an MCB without RCD protection and those fed from an RCCB with no other means of protection back to the cutout.

Edit: Just realised this isn't the thread I thought it was 😂
 
Last edited:

Reply to RCD protection upstream?… in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Question is does this DB really need RCD protection as there are only internal lights and sockets supplying this large building that used to be a...
Replies
13
Views
564
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Evening all, If a socket circuit is not RCD protected via an RCD/RCBO and there isn't the option of fitting an additional RCD enclosure or...
Replies
20
Views
6K
Can anyone tell me the latest regulation for RCD protection on socket outlets, I believe it's required for sockets up to 32A but I'm told it...
Replies
4
Views
2K
Afternoon everyone, I have a quick question about the Tesla Gen 3 Wall Charger? Does it require Type A 30MA RCD protection or not. Only because...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock