hi i was on a fuse board change to day and the new fuse board was switch off and no buzz bar connected and no tails connected but 1 of the circuits which was a radial to the kitchen when you put the neutral in it tripped the rcd can any 1 tell me why :lightbulb:
 
Did you do any test before you wacked the new CU in, think anther post gives a good few steps to so before getting the new CU out of box
 
but there is no voltage on the cable but the job was 2 houses knock in to 1 but that was done years ago

I hope others will correct me if I'm wrong but even if the circuit is not live (MCB open) the RCD can still trip if there is a neutral/earth fault.
 
As happyhippydad says, the RCD can trip with the circuit MCB off if there is a N-E fault, but the RCD must be energised from somewhere - try pressing the test button on a not-yet-fitted RCD - it won't trip. So there must be power coming from somewhere. Could the radial be getting it's live from the supply to what was the other house, and neutral from the one you are working from? (NOTHING would surprise me.) Then the circuit N would only have voltage if a) there was a load connected, and b) the circuit N was not connected to supply N or E.

Also, there must be something connected to the feed side of the RCD for there to be a path, and hence any current flowing through it.
 

Reply to rcd trip y in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
385
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
861

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock