Currently reading:
Safety question with stripping

Discuss Safety question with stripping in the USA Electrical Forum area at ElectriciansForums.net

Hemgs1

DIY
Reaction score
1
I have had a major house fire before, so I am a bit paranoid about electrical.

Recently we had a outlet where one of the wires came loose. Upon inspection I also notice the wires were stripped back pretty far. The house is 4 years old, but when we moved in last year noticed most outlet were wiggly in the wall and the dry wall looked like it got cut by a kindergartner with a butter knife.

I did tighten up the outlets right after we moved in but I didn’t check for loose connections. The recent situation is making me want to double check everything.

My biggest question is about the stripping, see attached photo, is it being cut that far back a safety issue? If so I may have to hire out someone to go through everywhere to fix it. If it is simply checking for loose wires I can do that.

Any advice is appreciated. Sorry if I’m being a bit paranoid, but I have no desire to deal with another fire or put my family at risk.
 

Attachments

  • 8CC8C21D-0FAF-4308-A062-EAE571B5D695.jpeg
    306.4 KB · Views: 81
  • FC363FBC-BB02-4490-A329-105D4AD81FF0.jpeg
    258.9 KB · Views: 82
  • A184FC03-DC52-4BFB-A353-9D5FEBD32378.jpeg
    287 KB · Views: 77
  • E10B5544-0EB9-4782-9F3A-29982E0AFE51.jpeg
    258.3 KB · Views: 76
Personally, i think that is a poor job.
I hope it is not the standard of most American wiring.

In the uk, it would not be acceptable.,

what do you think @Megawatt ??

p.s. i have asked for this to be moved to the American forum.
 
poor workmansip.the insulation on those cable should be tight up to the terminals. ( the ground wire on the green terminals is not so critical, but over her not acceptable. we would sleeve the bare ground wires. if yo feel confident, redo those connections that show bare copper ( making sure that the power is off before starting). if not, call in a qualified electrician to do it. megawatt is your best guide here. think he's actually in NC.
 
poor workmansip.the insulation on those cable should be tight up to the terminals. ( the ground wire on the green terminals is not so critical, but over her not acceptable. we would sleeve the bare ground wires. if yo feel confident, redo those connections that show bare copper ( making sure that the power is off before starting). if not, call in a qualified electrician to do it. megawatt is your best guide here. think he's actually in NC.
Ok. Essentially I would disconnect the wires trim them to correct length and reconnect?

i wouldn’t need to cut, restrip and connect right?
 
Ok. Essentially I would disconnect the wires trim them to correct length and reconnect?

i wouldn’t need to cut, restrip and connect right?
basically, yes. just cut the ends a bit shorter. do 'em 1 at a time so you don't get it wrong. over here we don't use those wrap round terminals, our's are more like this:
1608735239517.png
 
basically, yes. just cut the ends a bit shorter. do 'em 1 at a time so you don't get it wrong.
So what is the hazard with leaving them as they are? If it’s within code, I assume the hazard is less? I would assume it’s more a shock hazard than a fire hazard?

if a wire came loose and contacted something else that should trip a breaker right?

I am trying to determine the sense of urgency, not determine if it’s necessary.

Sorry for all of the questions. Having been through a fire I don’t want to go through that again.
 
If there's no nicks or indentation marks in the copper where the wire was originally stripped you can just trim it shorter and reterminate it. If the copper was indented where it was stripped then cut the end off and restrip the wire without damaging it.
 
I wouldn't class this as an immediate electrical or fire hazard, the hazard is some of the bare copper showing is long enough to come into contact with something it shouldn't and even more so if you've disturbed them. Yes the circuit breakers or fuses should protect the installation from damage by clearing a fault but it's such a simple thing to correct it would be a bit silly not to. It should be in the realms of a competent DIY'er who knows how to isolate the power to the installation to just to remove the wires one by one, check for damage and trim to a sensible length before reconnecting.
 
What would happen if the exposed copper on one of these wires touched dry wall?

you may be able to tell, but the boxes are poorly installed as well.

I think in NC I have 6 years to go back to a builder, but since it’s in code I’m not sure if they would be inclined to do anything about it and it’s not worth suing over.
 
If live exposed copper touches drywall nothing much will happen unless it gets damp, in which case the drywall surface could become live to the touch around the outlet. Copper touching anything other than the actual connection terminal is not really acceptable practice.

I don't know how the NEC codes it, but in the UK electrical regulations we have a catch-all that states that good quality materials and proper workmanship must be used. This can be used to call out installers for rough work even if it ticks the specific boxes. E.g. they put the right size and kind of wire in the right type of receptacles, but the insulation is chewed up or the screw threads are stripped or some aspect falls significantly short of what a competent electrician would be expected to achieve.

FWIW as mentioned above, in the UK we mostly use back-wired terminals with recessed screws, so it is unusual to see any live metal that can be touched, and the same goes for the ends of the wires. I normally make the insulation stop about 1/8" into the entry funnel of the back-wiring port. You could literally run your fingers all over a live switch or outlet removed from the wall without getting shocked.
 
The problem could be if the drywall has been constructed with metal uprights and noggins and the live copper touches one of the those, then anything connected to it could become live, any metal objects screwed to the wall also have the potential to become live including metal pipework and anything fitted to the pipes: taps waste traps etc.
 
I have had a major house fire before, so I am a bit paranoid about electrical.

Recently we had a outlet where one of the wires came loose. Upon inspection I also notice the wires were stripped back pretty far. The house is 4 years old, but when we moved in last year noticed most outlet were wiggly in the wall and the dry wall looked like it got cut by a kindergartner with a butter knife.

I did tighten up the outlets right after we moved in but I didn’t check for loose connections. The recent situation is making me want to double check everything.

My biggest question is about the stripping, see attached photo, is it being cut that far back a safety issue? If so I may have to hire out someone to go through everywhere to fix it. If it is simply checking for loose wires I can do that.

Any advice is appreciated. Sorry if I’m being a bit paranoid, but I have no desire to deal with another fire or put my family at risk.
That is plum ugly with no pride in the so called electricians work. Install receptacles with back stabs instead of stripping that much wire to wrap around the screw. Actually in the US an inspector can fail a job if neat workmanship is not applied
 
If live exposed copper touches drywall nothing much will happen unless it gets damp, in which case the drywall surface could become live to the touch around the outlet. Copper touching anything other than the actual connection terminal is not really acceptable practice.

I don't know how the NEC codes it, but in the UK electrical regulations we have a catch-all that states that good quality materials and proper workmanship must be used. This can be used to call out installers for rough work even if it ticks the specific boxes. E.g. they put the right size and kind of wire in the right type of receptacles, but the insulation is chewed up or the screw threads are stripped or some aspect falls significantly short of what a competent electrician would be expected to achieve.

FWIW as mentioned above, in the UK we mostly use back-wired terminals with recessed screws, so it is unusual to see any live metal that can be touched, and the same goes for the ends of the wires. I normally make the insulation stop about 1/8" into the entry funnel of the back-wiring port. You could literally run your fingers all over a live switch or outlet removed from the wall without getting shocked.
@Lucien I can’t see a viable reason that the wire manufacturing factory’s don’t put insulation on the ground wire in Romex. As you say it is dangerous and I can’t count how many times I’ve been shocked with the way our devices are made
 
So I was replacing outlets and on one of my outlets I nicked up the copper pretty good so I trimmed it off and restriped it. My question is if one hot wire going into the outlet is longer than the other one, since I have to cut one twice, does that matter?

I can’t believe it would, but I figured I would ask to be safe.
 
So I was replacing outlets and on one of my outlets I nicked up the copper pretty good so I trimmed it off and restriped it. My question is if one hot wire going into the outlet is longer than the other one, since I have to cut one twice, does that matter?

I can’t believe it would, but I figured I would ask to be safe.
Never cut the wire unless it’s burnt. By code you should have 6 inches of wire hanging out of all boxes
 
That is plum ugly with no pride in the so called electricians work. Install receptacles with back stabs instead of stripping that much wire to wrap around the screw. Actually in the US an inspector can fail a job if neat workmanship is not applied
"Yeah but I can smash out four a day bro and I'm never shrot of work. Earning megabucks, buying oversized site radios, blazzin tunes to annoy you slow old farts."
 
Never cut the wire unless it’s burnt. By code you should have 6 inches of wire hanging out of all boxes
intresting. here 6" of wires hanging out, we'd never get them into the boxes. some light switch boxes are only 5/8" deep. (most of us try and use 1" boxes for switches, or deeper for dimmers /smart switches).
 
In the UK most electrical work is in older properties where solid walls are the norm and metal box's have to be recessed into the brick or block, hence the 1" deep, or at most 1.3", on more modern construction where we have started to follow the US trend for timber studding larger box's can be used, but are not readily available.
 

Reply to Safety question with stripping in the USA Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

USA Electrical Advice

Welcome to the USA Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.

UK Electrical Forum

This is the main UK Electrical Forum at ElectriciansForums.net. Electrician State Laws for Electrics and Electricals may differ on a state-by-state basis. American questions and answers can be found in our UK electrical forum.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock