Discuss Serrated washers on steel conduit in the Electrical Appliances Forum area at ElectriciansForums.net

Reaction score
145
Whats the opinion in serrated washers with galv steel conduit? I was always taught at college to have one in between coupler and accessory and coupler and trunking, wether being used as the cpc or a separate cpc.

I was at a job today where they are installing a trunking/conduit system but are not using serrated washers, I mentioned it but basically got told to shut up! Couldn't really come up with a good answer, they just said it's not being used as the earth. I said it could carry significant fault current so the system need some to be mechanically and electrically sound.
 
Isn't that why we bond the trunking or metal box or conduit box that said conduit is attached to? I've never used serrated washers or been told to do so.
 
I'm interested to hear what others think about things like this. We are taught that metal conduit and trunking must be earthed regardless of whether or not it is used as a c.p.c. (as it is an exposed conductive part) and that you should achieve electrical continuity throughout the containment system. However, we have not been taught to use of serrated washers. Another one is scraping paint of metal backboxes etc. Reminds me to refer to the text books I have (mixture of old JTL/CITB and some new) and see what is said.
 
I like seeing serrated washers as you say just because a separate cpc is incorporated it is just important the conduit is effectively earthed. Of course a correctly installed system should ensure continuity but I do like them.
 
I like to see them aswell, but not a good reason. If it was my job they would be fitted, but not much I can do!
 
I went in the wholesaler the other to get some for a large swa gland, the look of dismay from the bloke behind counter was priceless. He said we dont stock any serrated washers....
 
Never used them in any conduit system. Why would a competently installed conduit run with threaded fittings require serated washers for earth continuity?

Anything painted I rather get good contact with an earth prep tool like G&j Hall manufacture.
 
Never used them in any conduit system. Why would a competently installed conduit run with threaded fittings require serated washers for earth continuity?
Same, folk can't be arsed today to spend a bit of time cleaning the accessory up to obtain good continuity.
 
Okay, what the hell is a serrated washer.?
They're known as star washers in this neck of the woods. Generally used to provide a mechanical lock for a nut especially in a vibration environment. Do they actually do anything to improve earth impedance on steel conduit systems? I've never seen them specified to improve the impedance of a joint, my initial thoughts would be that they may even decrease the contact area or maybe could strip the galvanising off one of the surfaces and accelerate corrosion so could even be detrimental... (**tin hat on**)
 
Just googled it, and can say don't see the connection with conduit work or any kind. Never used them in my day.
Here,here
Not only have I never seen or heard of washers (serrated or otherwise) being used on a conduit system,the action of introducing two extra surfaces to retain continuity (where no action should be required) seems to be making the continuity and effectiveness of passing a high current worse.
If it was the case it is a better practice why were we not doing so decades since
 
If it was the case it is a better practice why were we not doing so decades since

I thought that we were. My understanding that in England the method was different in Scotland, so I'd be interested hearing from Scottish members.
 
I've always used flanged couplers that incorporate a lead washer for when I used to install conduit systems. Although that was also a requisite for the M&Q regs I was working to at the time.
 
All right I know I'm going to get some sheet over this, to answer a question someone posed the reason why they didn't use these things years ago was/is because installation standards have gone by the wayside, how many sparkys clean the ends of couplers when used as an end to be fitted into an accessory? how may file the lock nut? how many clean the paint from an accessory box? go figure.
 
I thought that we were. My understanding that in England the method was different in Scotland, so I'd be interested hearing from Scottish members.

Wales is my experience, but I would have thought the whole of the UK was more unified back then,especially trade practices concerning serrated washers :)
 
Looks like I don't really have an argument.
 
Where did you go to College Rocboni? I'm from the same area as you and I'm sure we were taught to use them at college. Also, it was standard practice when I worked for a large contractor in Glasgow. As was lock rings behind couplers, which you don't always see.
 
Scottish Borders.
 
You'll have been taught by Kenny Redpath then?
 
Yes but no longer teaches, used to come in to cover the odd day right up to last year, he's got two young (less than 5) kids and an Asian wife!

Who did you serve you're time with?
 
Last edited:
Blimey! He did have a young Asian 'friend' when I was there.
We used to call him Yoda! Malcolm Hood was the other one who taught us but he's back on the tools now.
 
I occasionally come across installations where serrated washers have been used, but they are normally older installations not recent ones.
A local theatre has a conduit installation where serrated washers were used throughout and I think that part of the installation dates from the 1970's
 
Our college completed in 2012 has them on everything, so still goes on, I do like them but doesn't look like I can justify them really.
 
Serrated washers should be used in conduit/trunking installs. If you are fitting a complete c/t install why use earth cables ? Serrated washers at the trunking/bushing only side is acceptable where conduit forms part of a surface installation.

I dont get why anyone would design a metal c/t install with earth cables unless the place is prone to corrosion.
 
The system in this particular install was designed by building services consultants and contains cpc's for all circuits. But I do agree, I personally don't think it makes a difference wether it has or not, I like to see the washers!
 
Serrated washers should be used in conduit/trunking installs. If you are fitting a complete c/t install why use earth cables ? Serrated washers at the trunking/bushing only side is acceptable where conduit forms part of a surface installation.

I dont get why anyone would design a metal c/t install with earth cables unless the place is prone to corrosion.

And if it is prone to corrosion then steel containment is not the most suitable solution
 
Serrated and spring washers were mainly used for security as Marvo has said.
Locknuts used to be common too , Along with castellated nuts and split pins.
Then came the nyloc..
 

Reply to Serrated washers on steel conduit in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Hi, My first post so hopefully I am correct in posting it here. My question is, I am thinking of an IP rated outdoor socket for the back garden...
Replies
3
Views
1K
Is anyone aware of any galv trunking that is smaller than 50x50. I'm drawing a blank online. I've taken over a job that's used 16mm twin and earth...
Replies
12
Views
865
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
791
A recent discussion on conduit choice wandered over to pros and cons of the 'conlok' style and a link was posted to one of the Efixx videos in...
Replies
29
Views
4K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock