Search the forum,

Discuss Steel Container/cabin with PME supply in the UK Electrical Forum area at ElectriciansForums.net

Aaron b

Mentor
Esteemed
Arms
Reaction score
334
Hello, Where I work there's a steel cabin that other employees have installed and powered up without certification. Am I correct in thinking it's covered under part 717.411.4 that it can not be connected to a PME supply? I've been asked to test it and I'm concerned with the design and installation of the supply. With how easy it would be to TT I don't feel the risk is worth it even if it wasn't covered by 717.
 
Do either of the exceptions in 717.414.4 apply - is it under continuously supervised by skilled or instructed person(s), and was the earthing checked before it was connected. (You said it wasn't certificated; was it tested?)
 
Last edited:
Hello, Where I work there's a steel cabin that other employees have installed and powered up without certification. Am I correct in thinking it's covered under part 717.411.4 that it can not be connected to a PME supply? I've been asked to test it and I'm concerned with the design and installation of the supply. With how easy it would be to TT I don't feel the risk is worth it even if it wasn't covered by 717
what where they thinking faraday cage .
 
As far as I'm aware no testing has been completed. There is no management system detailing supervision or instruction, it's just a cabin used as storage with heating and lighting and I think it is reasonable to think any employee could use it.

Would these exceptions be for exceptional circumstances such as where the task would make a TT system impractical and testing would be conducted before each use? I struggle to see how an instruction would make the loss of a neutral less hazardous unless it was switched off before touching the true earth.

It's also appears to fed from a 32a socket that doesn't appear to be RCD protected. I think it's reasonable for me to refuse to test it.
 
Thanks, I suppose that's true. Should I conduct live testing though as surely it would fail on inspection? The main building has a couple of extraneous conductive parts not earthed, steel braces from the building that has recently had conductive parts installed near it and a new gas main. Would it be a bad idea to live test without that being sorted first?
 
I think these days a 230V/400V outdoor plug/socket without 30mA RCD protection would be a C2 on any EICR inspection. Not sure how that would apply to your site though.

From my own limited experience of these sort of cabins they usually have a 30mA incomer, so TT'ing is easy. But you would need an acceptable rod or similar for earth, and you also have the risk of a fault L-E before the RCD which might be worse than the PME risk depending on how the cable is routed into the cabin and the quality of the electrics there.
 
Thanks for everyone's input. Hopefully I can get them to make it safer by fitting a RCBO to the socket and TT'ing the cabin.
Just think about it a lost neutral on the DNO side the metal would become live the first thing any body would do is to open the bloody metel handle so they would become live straight. way.
 
It’s slightly grey in my mind whether a 32A outside socket would attract a C2, as before 18th edition I think anything over 20A wasn’t required to have RCD protection. I’d like it to be a C2!
In this case it’s effectively an extension to the installation as the thing will never get unplugged, so the circuit supplying it should be up to current regs.
I’d insist on the RCD protection.

The risks of likelihood and consequences of pen fault versus TT and RCD failure are interesting.
With no data, if forced to place a bet, I’d go with the RCd never being tested and getting stuck one day as more likely to happen. But losing fault protection only matters in a fault, going open pen in this situation is always going to be serious. I’m not a “just TT it” person but I think it’s justified in this situation.

I’d like to see more affordable pen protection devices (as per car charger market) so the benefits of low impedence earthing can be retained in these situations.
 
It’s slightly grey in my mind whether a 32A outside socket would attract a C2, as before 18th edition I think anything over 20A wasn’t required to have RCD protection. I’d like it to be a C2!
In this case it’s effectively an extension to the installation as the thing will never get unplugged, so the circuit supplying it should be up to current regs.
I’d insist on the RCD protection.

The risks of likelihood and consequences of pen fault versus TT and RCD failure are interesting.
With no data, if forced to place a bet, I’d go with the RCd never being tested and getting stuck one day as more likely to happen. But losing fault protection only matters in a fault, going open pen in this situation is always going to be serious. I’m not a “just TT it” person but I think it’s justified in this situation.

I’d like to see more affordable pen protection devices (as per car charger market) so the benefits of low impedence earthing can be retained in these situations.
It's not just a C2 though as although the electrical install in the cabin is existing the supply is new so as far as I'm aware can't have any non conformities unless declared by the designer. I've brought in my big hammer and my mft so I'll see how it goes.
 
I’d like to see more affordable pen protection devices (as per car charger market) so the benefits of low impedence earthing can be retained in these situations.
Had these years ago - voltage operated earth leakage breakers. Modern version would have to be three pole rather than two, though, to break the earth as well.
 
Had these years ago - voltage operated earth leakage breakers. Modern version would have to be three pole rather than two, though, to break the earth as well.
Ah yes, but those things had a number of flaws including needed a working earth to work at all didn’t they, as it was a coil between the energised earth conductor and real earth that triggered the trip?

I think there's now an ÂŁ80 ish solution from CityVolt that looks interesting, as it's getting towards the price point where customers could be convinced into having one....
 
Answer is found in GN8 10.5.6 (717.411.4) - "Regulation 9(4) of the ESQCR prohibits a distributor's combined neutral and protective (PEN) conductor (from a PME network) being directly connected to any metalwork of a caravan. For safety reasons, the same requirement also applies to mobile and transportable units, with certain exceptions, as stated in Regulation 717.411.4 of BS7671..... [Another] precaution that can be taken is the connection of earth electrodes to the main earthing terminal (MET)....."
 

Reply to Steel Container/cabin with PME supply in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock