Currently reading:
Triton T80GSI Electric Shower With Equiopotential Bonding

Discuss Triton T80GSI Electric Shower With Equiopotential Bonding in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
Hello, I have a customer who is looking to replace their electric shower. There is equipotential bonding connected to the cold feed. I’ve not seen it within an electric shower before.

I was wondering if it has to stay or if it can be removed? The customer is considering changing the model of the shower and there may not be enough room to leave it within the shower like it currently is. Thanks
4eeee573-41d5-4603-9a1d-1290ab14dd7e.jpeg
 
Last edited by a moderator:
You really need to read 701.415.2. - if you meet all three conditions it isn’t required.
But too much to summarise!

If keeping it, it can be connected close to the point of entry to the room, it doesn’t have to be within the shower itself.
 
Last edited:
You really need to read 701.415.2. - if you meet all three conditions it isn’t required.
But too much to summarise!

If keeping it, it can be connected close to the point of entry to the room, it doesn’t have to be within the shower itself

Thanks for the reply, Tim. Most appreciated. I have another question if that’s ok?

I can see that the earth wire from the 6mm cable is connected to the earth clamp. What is the larger earth wire that’s going into the terminal on the electric shower?
 
Thanks for the reply, Tim. Most appreciated. I have another question if that’s ok?

I can see that the earth wire from the 6mm cable is connected to the earth clamp. What is the larger earth wire that’s going into the terminal on the electric shower?
There's the bond

There's also the supply earth and that connects on to the heater tank of the shower
 
It looks to me as though here is a good chance the pipe is an extraneous conductive part and will require bonding somewhere near by. It looks as though the CPC of the shower circuit was used to support the bonding.
(I was thinking about omitting supplementary bonding in my original reply as I didn't look at the photo carefully enough.)
 
It looks to me as though here is a good chance the pipe is an extraneous conductive part and will require bonding somewhere near by. It looks as though the CPC of the shower circuit was used to support the bonding.
(I was thinking about omitting supplementary bonding in my original reply as I didn't look at the photo carefully enough.)
So would you say it is best to leave it all in place when the shower is replaced? Would it benefit the customer to have an electrician look at it?
 
So would you say it is best to leave it all in place when the shower is replaced? Would it benefit the customer to have an electrician look at it?
It most likely would have been done for a reason.

Leave it there, as without testing, you can't tell if the water supply pipe is bonded or extraneous.

You will always benefit from having a competent electrician look at it.
 
Work in a special location needs registration under the requirements of part p in the building regulations. I believe this is a moot point as far as discussions go, this is a job for an electrician so the entity of the supporting electrical systems can be assessed for the change of model and / or safety assessed re continuing use and finally worked on legally. Bit like asking questions about which prescription doses you need for an illness , it needs a registered professional to assess, no exceptions.
 

Reply to Triton T80GSI Electric Shower With Equiopotential Bonding in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock