Currently reading:
How to fit SY glands.

Discuss How to fit SY glands. in the Commercial Electrical Advice area at ElectriciansForums.net

M

Martinm

Hello folks,

SY glands for SY cable have came to my attention in work, can anyone shed any light as to how these are correctly fitted, It looks and sounds straight forward. does the screen come into play somehow?
 
Hi martinm

If you use those glans with the slots on the threaded end: put the gland in the panel hole, strip the cable back so that the shield is approx 2" free, make two
halves out of the braid, twist it to sort of a wire, put one of the brass rings on the other side of the gland (threaded side) push the cable with the two braid bundles through the compression side and fold the braid into the slots, put the second brass ring over it and then secure the gland to the panel with the lock nut. Hope this helps.

Cherio. Stef.
 
look on YouTube;The Practical Skills Series : Cable Termination - SY Flex ["Electrical Jobs" / Electrician]


SY glands for SY cable have came to my attention in work, can anyone shed any light as to how these are correctly fitted, It looks and sounds straight forward. does the screen come into play somehow?[/QUOTE]
 
Last edited:
I have also seen sy terminated with a standard compression gland with the braiding twisted and covered with earth sleeving.
 

Reply to How to fit SY glands. in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top